What capacity must the heat pump have?

  • Erstellt am 2019-04-17 20:44:30

boxandroof

2019-04-18 09:40:19
  • #1

If these are two separate units, two heat pumps and two separate hydraulics are advisable. You can then operate two heating curves without a buffer tank or ERR, and the residents can set the apartments to different temperatures. Especially if you rent them out later, this otherwise causes problems. If you buy them yourself, the heat pumps only cost 2x €3,000.

Regarding noise:
Only at 60% heating output (approx. 3kW) and simultaneous subzero temperatures does it become audible. Above that, the noise level increases significantly; below that, it is practically inaudible. Nevertheless, I would install a privacy screen toward the neighbor directly or even earlier, because what you see you hear, and visually the Panasonic is not a highlight either. During drying, it ran with 5kW for a long time at our place, and it stands acoustically unfavorable in a corner here; the neighbor could hear it at night (20m, old windows).

Ours is now limited by whisper mode to about 60% output (approx. 3.3kW); with defrost cycles it does not manage more than 2.5kW on average during the day. I let it run freer (4kW) for a few hours during the day by timer. You cannot limit it below 3kW, meaning that it is slightly audible in any case when it’s cold, but the difference compared to 5kW output is very large. In general, Panasonic is considered very quiet. I don't know other heat pumps and can only report from ours.


On the contrary, the idea is excellent. Do it that way! Oversizing is a problem with non-modulating or poorly modulating heat pumps because it leads to many heating cycles. The current Panasonic 5kW model (H in the type designation) modulates down to about 1.3kW heating output (at <200W power consumption). If you lower the heating curve at night by timer, which is recommended anyway, it won't start at night during transitional periods at all. This effectively halves the heat pump’s capacity and places the possible noise load into the day. It will not cycle if the rest of the hydraulics are correct. My observation is that it runs not only quieter but also more efficiently in the modulation range.

Alternatively, you can design the hydraulics so that you first try with one heat pump and later completely separate the two hydraulics with a shut-off valve. For that, however, it's better to visit the HTD forum.
 

Similar topics
26.10.2017Experience values for the sound level in dB_A of a central controlled residential ventilation system14
14.02.2024Bafa funding for heat pumps will be discontinued as of 31.12.2020.508
14.05.2023How did you install your heat pumps?15
08.02.2022How complicated are heat pumps in practical operation?78
16.04.2022Which air-to-water heat pump is suitable for new construction?13
09.04.2023Planned throttling of wallboxes and heat pumps34
26.05.2025Which heating system for a multi-family house, heat pump not eligible for subsidies?23
30.07.2023Heat pump theft protection - Covered by building insurance?36
04.03.2024Costs for heat pump and photovoltaic in 2024 in small old buildings20

Oben