Vapor barrier connection foot purlin / sealing

  • Erstellt am 2019-04-29 12:13:23

Mat91

2019-04-29 12:13:23
  • #1
Hello everyone,

we noticed today during the Blower Door test that we apparently connected the vapor barrier incorrectly. Just a brief introduction: we built a two-story house with a hip roof and a 35° roof pitch. The heating and ventilation system is located in the attic. Therefore, we insulated both the wooden beam ceiling on the upper floor and the attic with 24 cm insulation and Isover vapor barrier.

Now to the issue. We glued the vapor barrier in the attic to the collar beam. This rests directly on the ring beam. During the Blower Door test, it was noticed that air flowed between the collar beam and the ring beam into the attic. I have now learned that we should have glued the vapor barrier up to the masonry.

How should we proceed best now? Would it possibly be sufficient to inject and seal the collar beam with silicone? The attic is only used as a storage space and for housing the heating/ventilation system. Or should I cut a 30 cm strip of the foil and connect the collar beam to the masonry?

I quickly made a sketch for better illustration. I would appreciate your tips.
 

Lumpi_LE

2019-04-29 12:20:57
  • #2
You have already sealed the [OG] against the [DG]? And it still drafts in the [DG]? Then there must be something else wrong, or how is the sketch to be understood? Otherwise, without knowing any other boundary conditions, the second option (new strip) would be the correct approach for now.
 

Mat91

2019-04-29 12:30:31
  • #3
Thank you for your quick response, I have uploaded another picture with the plan from the architect.
 

Lumpi_LE

2019-04-29 13:29:46
  • #4
Is the intermediate ceiling insulated? Who came up with that? The arrangement doesn't really make sense. Regardless, it probably shouldn't matter for the blower door test, since apparently you do have a hole in the sealing to the attic, which is much more serious.
 

Mat91

2019-04-29 13:54:37
  • #5
Exactly, the intermediate ceiling is also insulated. The roof had to be insulated because of the heating. We wanted the upper floor to be additionally insulated for soundproofing (all done by ourselves). It certainly won't hurt to have both insulated.

If we now extend the vapor barrier up to the ring beam, the problem should be solved, right? I had possibly hoped that the much simpler solution (sealing with silicone) would also be OK here. But we'd rather do it properly once.

Just to be sure again. We did the blower door test once with the attic stairs closed. Everything was fine then. In another test with the hatch open, there was a draft noticeable between the ring beam and the foot purlin.
 

Lumpi_LE

2019-04-29 14:11:34
  • #6

If not heated and not ventilated, it can indeed cause damage. It is definitely not particularly beneficial for the wooden structure.
Make sure to set up a temperature/humidity meter with a logging function.


Oh, okay, then it doesn’t sound so bad anymore.
Silicone is not permanently airtight.
 

Similar topics
02.09.2013Which heating system for prefab houses: air source heat pump, geothermal, solar, photovoltaic17
25.07.2014Energy saving regulation without heating10
09.05.2016Compliance with the 2016 Energy Saving Ordinance with the following heating14
29.04.2016Which heating? Please provide recommendations27
03.11.2016Which heating system to choose when replacing the heater after 36 years?24
15.08.2017Calculation interior finishing: heating, sanitary, bathrooms, floor coverings55
31.08.2017Do you turn off the heating completely during vacation?24
01.01.2018Which control system? Control heating/ventilation/air conditioning with an app31
18.02.2018Heating broke down 2 weeks after expensive maintenance - Tank cleaning?17
12.08.2018Insulate the top floor ceiling without a vapor barrier17
14.09.2018Heating (Heat Pump) Incorrect, heat output too high?14
25.06.2019Heating defective due to ammonia from the channel15
12.08.2019The agony of choice in heating16
14.09.2020Vapor barrier roof - tape stapler nails?10
14.12.2022Insulate cold roof attic for office23
20.02.2023Building defect cold bridge at the ring beam?12
15.05.2023Development plan: Definition of attic11

Oben