Underfloor heating: Length of heating circuits

  • Erstellt am 2019-09-11 11:44:21

Detlev69

2019-09-11 11:44:21
  • #1
How long would the experts here choose the individual heating circuits of the underfloor heating?

I need about 1350-1400 m total length. With 12 heating circuits, that still results in a good 112 m per circuit. Is that too long or OK?

Can someone estimate what pressure loss occurs over 112 m with 16x2 pipe?
 

Lumpi_LE

2019-09-11 12:11:27
  • #2
There are people who calculate that for you. Pressure loss depends on many factors and cannot be answered in general terms. 112 m 16er Rohr is already borderline..
 

User0815

2019-09-11 12:28:01
  • #3
I have actually read everywhere that a heating circuit should not be longer than 100m, and I have adhered to that.
 

Bookstar

2019-09-11 19:09:05
  • #4
Brevity is the soul of wit!
 

boxandroof

2019-09-11 19:14:50
  • #5
Have 80m +/-10% everywhere. Avoid particularly long loops, especially in rooms with high heating load, such as the bathroom.
 

Michlhausbauaa

2019-09-24 08:41:14
  • #6
Let a professional assess that.
 