The U-value calculator even knows Armaflex. If you enter all your layers there, such as gypsum plasterboard, glass wool with battens, vapor retarder, glass wool, Armaflex, spruce, roofing membrane, slate, you can see 4 things (if you want to use the Armaflex).
You have to be extremely careful that the vapor retarder is really airtight, so that no moisture can get into the wool (if using Armaflex and without ventilation as in your original proposal).
It must not be too airtight either, because the top is vapor-tight (if the Armaflex is behind the insulation).
Without ventilation due to your existing spruce/bitumen layer, it will not work.
And regardless of that, I would not clamp the vapor retarder between both insulation wools. Under unfavorable indoor humidity conditions, you have condensate in the 40mm insulation layer.
Actually, the approach should be:
Gypsum plasterboard, vapor retarder, glass wool with battens, glass wool ventilation, roofing membrane, slate