New construction KFW55 house - heating design, different statements

  • Erstellt am 2020-12-05 13:15:13

T_im_Norden

2020-12-06 07:53:18
  • #1
The heating engineer normally thinks in such a way that he has as little work as possible with the customer and not that the customer heats as sparingly as possible.

With a well-designed underfloor heating system, you normally always have enough water in the heating circuits to defrost an air-to-water heat pump.

The reason why buffers are still often installed lies with the individual room controllers; through their switching behavior, they repeatedly cause entire rooms to be shut off.
If the defrosting process is to take place, it can happen that so many rooms are shut off that there is no longer enough warm water available.
The result is that the heating system goes into fault mode.
If the heating engineer, on the other hand, installs a buffer, he ensures that there is always enough water.

Those who have read up on heating with a heat pump and underfloor heating, on the other hand, will not use the ERR and therefore do not have this problem at all.
 

T_im_Norden

2020-12-06 08:03:24
  • #2
More important than the question of which heat pump you choose is the question of the underfloor heating itself.

Anything you do wrong here you cannot fix anymore.

A heat pump or the installation above the screed can always be changed, but everything that lies in the floor cannot.

Therefore, have it calculated externally with your house data.
 

T_im_Norden

2020-12-06 08:18:31
  • #3
https://www.hausbau-forum.de/threads/lwwp-dimensionierung-im-neubau.36049/page-21
 

DE_Haus

2020-12-06 09:35:53
  • #4
T_im_Norden first of all thank you very much for the information. I will read up on this thread Dimensionierung. We have an external KFW consultant, I think he can also calculate the underfloor heating.
 

nordanney

2020-12-06 10:30:36
  • #5
Find a suitable engineering firm that does nothing else. The KfW consultant is usually the wrong contact person and has no idea about the topic.
 

Similar topics
13.06.2012Underfloor heating and mechanical ventilation with heat recovery (MVHR), replacement of ordinary radiators23
20.10.2016Water-bearing fireplace stove floor heating, heat pump, photovoltaic, new construction?28
19.09.2023Cooling via underfloor heating with brine heat pump45
25.11.2015Offer air-water heat pump including underfloor heating, ok?19
18.04.2016Heating circuits/thermostats for living/dining/kitchen with underfloor heating/heat pump35
08.10.2017KfW 55 without underfloor heating38
06.06.2019Cooling in summer with air-to-water heat pump, underfloor heating and/or ventilation system?29
24.07.2019Energy Saving Ordinance 2016 or KFW 55 for bungalow with air-water heat pump & controlled residential ventilation, optional photovoltaic47
27.01.2020Properly setting the air-to-water heat pump with underfloor heating54
20.12.2019Underfloor heating in the children's room? Some rooms planned without underfloor heating? Air-to-water heat pump removed?48
18.05.2021KfW energy calculation with cooling heat pump22
24.08.2021Cooling with heat pump via underfloor heating?117
17.07.2021Underfloor heating and air-to-water heat pump in new construction: am I going to have problems?28
08.10.2021Air-water heat pump combined with underfloor heating does not work properly65
07.12.2021Is a brine-water heat pump still worthwhile with KfW 40+?34
14.05.2022Old building apartment with gas boiler - underfloor heating now, heat pump later14
25.05.2022Air-to-water heat pump + underfloor heating + controlled residential ventilation with heat recovery - individually room differently temperature controllable?10
02.02.2023Individual room control with air-water heat pump and underfloor heating20
26.06.2023Heat pump, water storage tank, instantaneous water heater, wfK, underfloor heating, heating and cooling12

Oben