Hello everyone,
we have built a massive single-family house, 150sqm + basement; we have a heat pump Viessmann Vitocal-200s (also with cooling function), hot water storage 300 liters. Unfortunately, the heating installer installed the heating and did nothing, simply left the parameters as they were for hot water preparation and heating.
This is my first single-family house, I have always lived in multi-family houses with central heating, etc.
I have studied and read a lot and have now set everything like this.
Room setpoint temperature: 20°C
Heating time program: 0-24, no night setback
Hot water preparation setpoint temp1 06-08 42°C
Hot water preparation setpoint temp2 17-19 50°C (shower/bath time with children)
Circulation pump for hot water: 17-19 cycle 5/25 (the pump was running 0-24 with 5-25 cycle and I had very high electricity consumption)
Slope: 0.1
Level: -1K
Manufacturer settings were slope 0.5 and level 5K
Now the problem:
- at night naturally the house cools down, but I expect that the system regulates the temperature, e.g.
Yesterday evening I had 22°C in the living room, today morning at 5:30 I had 20.9°C; is this behavior related to the heating curve? Unfortunately, I have not yet received an introduction from the heating installer (move-in was in August);
I know that there is a specific procedure to adjust the heating curve, but unfortunately I have not yet done it.
Many thanks
Marco
we have built a massive single-family house, 150sqm + basement; we have a heat pump Viessmann Vitocal-200s (also with cooling function), hot water storage 300 liters. Unfortunately, the heating installer installed the heating and did nothing, simply left the parameters as they were for hot water preparation and heating.
This is my first single-family house, I have always lived in multi-family houses with central heating, etc.
I have studied and read a lot and have now set everything like this.
Room setpoint temperature: 20°C
Heating time program: 0-24, no night setback
Hot water preparation setpoint temp1 06-08 42°C
Hot water preparation setpoint temp2 17-19 50°C (shower/bath time with children)
Circulation pump for hot water: 17-19 cycle 5/25 (the pump was running 0-24 with 5-25 cycle and I had very high electricity consumption)
Slope: 0.1
Level: -1K
Manufacturer settings were slope 0.5 and level 5K
Now the problem:
- at night naturally the house cools down, but I expect that the system regulates the temperature, e.g.
Yesterday evening I had 22°C in the living room, today morning at 5:30 I had 20.9°C; is this behavior related to the heating curve? Unfortunately, I have not yet received an introduction from the heating installer (move-in was in August);
I know that there is a specific procedure to adjust the heating curve, but unfortunately I have not yet done it.
Many thanks