Lightning protection at the house, but how?

  • Erstellt am 2017-06-20 23:45:06

meister keks

2017-06-20 23:45:06
  • #1
Hello everyone, I currently have a small problem. My house has four gutters. Two are connected and the other two are just covers. The base plate of my house is equipped with a grounding rod. These protruded from the ground at each corner after the house was assembled. Now, out of ignorance, I cut off three and only have one left that can be connected to the gutter. Is that enough? Is one connection sufficient as lightning protection? Normally, two downspouts are installed on a house. Are always two connected? Best regards
 

Kaspatoo

2017-06-30 23:56:14
  • #2
Electricity seeks the easiest path if the "detour" via the gutter on the opposite side is now "more strenuous" than straight through the house... then you're out of luck, and who knows if a moody lightning strike might not pay a visit sometimes

but there are screw connections with which you can connect two steel band cables together speak, just reattach the cut cables, that's what they were for
 

Mycraft

2017-07-01 06:36:43
  • #3
The equipotential bonding in the floor slab has nothing to do with lightning protection...
 

Kaspatoo

2017-07-01 07:29:03
  • #4
He cut the connections to the gutters in three places, but I think he should restore them so that drainage is possible all around again.
 

Mycraft

2017-07-01 09:16:49
  • #5
No, he didn't... I read from the description that he cut off the connection tabs from the ring earth conductor. However, these have nothing to do with the external lightning protection in the broadest sense.

Everything in the house with a protective contact is connected to the ring earth conductor + at most the antenna system and not the external gutters.

These are connected to the external protection system and only then connected to the internal one.

And even if it now sounds as if everything is connected together anyway... there are reasons why it is supposed to be done this way and not otherwise...



But to get back to the initial question. Most likely it doesn't matter that you cut off three tabs. As long as you still have one in the HAR, everything is fine.

You don't have to connect the gutters to anything if you don't have a complete external lightning protection system.
 

Knallkörper

2017-07-01 09:42:31
  • #6
The effect of grounded gutters is likely minimal. However, I would say that they definitely belong directly to the [Fundamenterder].

If you now absolutely want to ground your downpipes but can no longer reach the brackets, you could instead drive a grounding rod / earth rod into the ground each. Pay attention to the material pairing due to galvanic corrosion.
 

Similar topics
21.10.2011Floor slab insulation "Yes!" or "No!"14
18.09.2012Construction of a base slab with frost skirt but without foundation10
31.05.2015Wastewater pipe concreted in the floor slab at the wrong location29
14.09.2012House financing - house, garage, and foundation slab approx. 290,000 EUR11
26.10.2012External perimeter insulation floor slab, basement mold risk11
21.11.2013Is the floor slab still possible this year?15
15.07.2014Foundation slab for Danwood bungalow? Company for complete works?11
25.04.2016Potential equalization? Ring earth or foundation earth...28
23.11.2014Stone throw on foundation slab - builder's liability insurance?16
15.06.2015Base slab or strip foundations for garage12
07.09.2015Minimum distance from the base plate?11
11.09.2016Base plate - construction/insulation etc. - experiences please!10
05.08.2016Leave the floor slab over winter15
20.08.2016Base slab vs strip foundation15
13.09.2016Insulation under the floor slab EPS or XPS?12
29.07.2018Perimeter insulation under the floor slab and still XPS under the screed?28
06.10.2016Base plate with defects?22
27.11.2016Double insulation below and above the floor slab?10
08.10.2017Ringerder, where is the best place to install it?10
28.04.2024Is lightning protection necessary for new buildings?11

Oben