LEDs for the suspended ceiling in the bathroom with 12 or 230 volts

  • Erstellt am 2020-07-09 18:54:38

hampshire

2020-07-12 10:07:02
  • #1
That doesn't make much sense. Just use a push button with an actuator right away. That the manufacturer advertises or approves the function for the model. We have installed Eltako actuators in the sub-distribution panel and placed a push button in front. That works.
 

Mycraft

2020-07-12 10:10:15
  • #2

Really series or parallel? Because own transformer speaks for parallel connection.


Depends on the dimmer.


Spots themselves don’t really matter. The important thing is the driver/transformer connected before. That’s what makes the difference.
 

hampshire

2020-07-12 10:18:12
  • #3
That is correct. Series connection only with central transformer and drivers designed for it. Addition: The dimmer must of course also be suitable as writes. A dimmer via resistor will not work, a phase-cut dimmer rather will.
 