Insulation of the base with WLG 025

  • Erstellt am 2021-06-25 10:32:09

neo-sciliar

2021-06-25 11:05:50
  • #1
okay....logical: 6 / 0.25 * 0.35 = 8.4. Therefore the question is whether 8 cm (mathematically it should be 8.4 cm) is sufficient, or whether it has to be 10 cm. The thermal resistance would then decrease from 2.4 to 2.29 m^2K/W at 8 cm, and the U-value would accordingly increase from 0.41 to 0.44.
 

Lumpi_LE

2021-06-25 12:05:58
  • #2
The question is rather whether it then doesn't protrude... what does the construction look like? PUR is available for inside and outside, you just have to keep looking.
 

neo-sciliar

2021-06-25 12:34:01
  • #3
We have a baseboard (Z-profile) that extends 12 cm beyond the floor slab. There is therefore space for 8 cm insulation and then plaster. With 10 cm it would be tight. Hence the question (above calculation) whether 8 cm WLG035 is sufficient.
 

Lumpi_LE

2021-06-25 14:12:57
  • #4
Base plaster is rather 5...10 mm, therefore 8 cm is no problem and usually also sufficient in practice.
 

nordanney

2021-06-25 16:33:54
  • #5
: The construction site is in Rhineland-Palatinate with you. If it’s not too far, take a look at smartbau in Nettetal. It is a second-choice dealer (where second choice can also mean that the boards are once a cm too short or too long) who exclusively sells PUR/PIR. They can currently deliver a lot at unbeatable prices.
 