Insufficient integration of joint plates?

  • Erstellt am 2020-06-16 17:03:04

bazinga

2020-06-16 17:03:04
  • #1
In our new construction project with a developer, we have an external building inspector who is overseeing the whole thing. The developer is building several terraced houses in this row, and after the basement slab was poured, the first defect appeared:

- The execution on site deviates from the requirements of the used joint sheet (FRADIFLEX)
- The sealing sheets are 15 cm wide and must be embedded 3 to a maximum of half their width into the concrete, that is 7.5 cm. Based on the films still attached at the upper area for protection, it is clearly visible that the embedding of at least 3 cm is not always provided.
- This is especially the case at the 4 corners, where significant height differences can be seen.
- In some places, film has been embedded in the concrete.

A few recent pictures:

[ATTACH alt="dsc07783.jpg" type="full"]48151[/ATTACH] [ATTACH alt="dsc07784.jpg" type="full"]48152[/ATTACH] [ATTACH alt="dsc07790.jpg" type="full"]48154[/ATTACH][ATTACH alt="dsc07793.jpg" type="full"]48155[/ATTACH] [ATTACH alt="dsc07814.jpg" type="full"]48156[/ATTACH]

Attached is the excerpt from the purchase contract: "The basement floor slab will be made of watertight reinforced concrete. A perimeter insulation will be installed beneath the floor slab. The basement level will be constructed as a white tank (usage class A). On the outside, in the joint area, a PMB waterproofing (plastic-modified bitumen thick coating) will be applied."

Tomorrow we will discuss this with the site manager and the external inspector. What is the experts’ assessment here? What problems could arise in the long term or can this defect still be corrected in some way?
 

Jann St

2020-07-10 18:11:34
  • #2
Hi,

I am obviously late now, but I am still interested in the result of the inspection.
In my opinion, the partially insufficient installation height is not a catastrophe. It is difficult to see from the pictures whether the reinforcement touches the sheet metal. This should definitely be avoided.
If damage occurs there, it can only be prevented from the outside later on. At that time, a resin hose could have been inserted as a precaution.

Your construction description is somewhat difficult in my eyes. The term "white tank" is only meaningful if the WU guideline was agreed upon. This is not apparent here. The statement usage class A likewise. You should check exactly what you are getting.

If you have any further questions, I’ll be happy to help.

Best regards
Jann Stöter
 

Similar topics
06.02.2013Developer says: No more insulation!12
23.03.2011Developer or architect?15
26.09.2011Finding tiles from other manufacturers / sample selection for builders13
09.07.2012Developer offer for single-family house - Are the construction costs acceptable?16
16.07.2012The builder "outsources" fixed-price services to subcontractors12
03.08.2012Contract Supplement to the Construction Contract by the Developer36
30.09.2012Developer - Is withdrawal from the purchase contract possible?11
01.12.2014Real estate transfer tax / what is the tax applied to? Which developer MUST?30
18.02.2014Massive problems with the builder - is contract termination possible?33
23.06.2014Developer charges heavily for replanning - justified?12
08.10.2014How do you search for a suitable property developer?30
27.02.2015Construction project with a developer without an official building plan, is a down payment required?12
01.03.2015The developer does not build according to the plan14
15.04.2015Duplex construction: Joint or separate developer?20
13.06.2015New construction with developer / construction drawing documents23
09.09.2015Buy land separately from the developer13
15.09.2019Developer refuses to hand over documents32
16.08.2020Bathtub misaligned - defect?15
06.04.2023White tub - Water exposure class W2.2-E19
22.12.2024Floor plan changes for end-terrace house from the developer133

Oben