How can information such as the Energy Saving Ordinance 2016 be accessed?

  • Erstellt am 2016-01-02 17:54:39

pius123

2016-01-02 17:54:39
  • #1
Is there anywhere layperson-understandable information from which one can see for oneself by which construction measures the conditions for the Energy Saving Ordinance 2016 can be met?

For example, if I want to build with Poroton bricks without additional insulation plus a heat pump plus a ventilation system, I would be interested to know how the dimensions would have to look for it to work - without having to consult a mathematics professor.

Regards Pius
 

Legurit

2016-01-02 22:35:48
  • #2
In case of doubt, this also depends on other factors such as the insulation of the remaining parts of the building. Furthermore, it depends on the type of brick. Very abstractly, an average 425 T8 or 365 T7 brick is sufficient for you.
 

Portoalegre

2016-01-06 13:19:04
  • #3
I would also like to have such information. Basics for me. Single-story on slab WF approx. 110 sqm 2 people Monolithic and gas condensing boiler a must What additional technology must be installed according to the Energy Saving Ordinance? Best regards. Portoalegre
 

Legurit

2016-01-06 13:44:34
  • #4
how is one supposed to answer that - or how is one even supposed to be able to help in any way? "I'm building a house, how much does it cost and what do I have to do for the energy saving ordinance" .. huh?! Do you have a construction service description? Are you building with a planner? Just read through the construction service descriptions of the big [GÜs] - they are available online. That gives you a relatively good idea of what is enough for what and what is not.
 

Bieber0815

2016-01-06 20:26:01
  • #5
I claim: No, there is not.

It is a complex topic, the requirement is "dual" (primary energy demand and transmission heat loss). In addition to insulation and airtightness of the building envelope (structural measures), the type of heat generation also matters. This can certainly be explained to a layperson, but the possible measures are diverse because they always have to be considered as a sum of various individual contributions.

My recommendation is to thoroughly read the relevant pages on kfw.de. "Effizienzhaus" is also a lemma on Wikipedia, likewise worth reading and of course with plenty of references (hyperlinks, unfortunately not allowed here, so you'll have to make the effort yourself ...) to the relevant keywords.

HTH
 

Grym

2016-01-06 20:33:12
  • #6
Your building will be compared with a reference building, where the transmission heat losses must be at least as good as those of the reference building and the primary energy demand must be 25 percent better. Primary energy demand should not be a problem with a heat pump. With a heat pump and controlled residential ventilation with heat recovery, it is not a problem at all.

The transmission heat loss remains. The reference values (U-values) are as follows:

Wall: 0.28
Roof: 0.20
Window 1.30
Ground slab/basement: 0.35
Equivalent performance must be demonstrated for thermal bridges; don’t ask me which TB catalog now.

If you want to exactly meet the limit values everywhere, then a brick with lambda 0.09 and 300mm or a brick with lambda 0.10 and 365mm or a brick with lambda 0.14 and 490mm will do. Alternatively, as minimal solutions according to reference values, 175mm KS-2.0 and 100mm EPS 032 work. A brick with lambda 0.07 would theoretically suffice with 240mm. However, this probably doesn’t work structurally.

In general, better construction has already been done in recent years. So there is no reason to worry.
 

Similar topics
18.07.2012What should be considered in a construction service description?10
31.05.2015Wastewater pipe concreted in the floor slab at the wrong location29
07.06.2013Is it mandatory to build according to the Energy Saving Ordinance (2009)?12
09.06.2015Gas, heat pump, and solar for a single-family house?36
19.06.2015Build according to KFW 70 or the Energy Saving Ordinance 201442
15.12.2019Aerated concrete exterior wall vs. Energy Saving Ordinance13
23.10.2015Energy Saving Ordinance 2014 - Gas boiler without solar?38
10.01.2017Energy Saving Ordinance 2016 / KFW55 / Gas + Solar in 201628
11.09.2016Base plate - construction/insulation etc. - experiences please!10
13.09.2016Insulation under the floor slab EPS or XPS?12
29.07.2018Perimeter insulation under the floor slab and still XPS under the screed?28
27.11.2016Double insulation below and above the floor slab?10
23.02.2017New construction according to the 2016 Energy Saving Ordinance no longer possible without a ventilation/exhaust system?40
27.02.2017Difference between Energy Saving Ordinance 2014 and Energy Saving Ordinance 201612
14.04.2017House construction from concrete vs Energy Saving Ordinance 201631
26.02.2018Insulation under reinforced concrete floor slab KFW5520
09.02.2019Ground slab with strip foundation and frost skirt23
13.12.2019Aerated concrete 42.5 lambda 0.08 or 0.0932
22.11.2020Final energy demand achievable without insulation13

Oben