a) How realistic is it to meet this deadline with our current situation and planned measures?
b) Or with which additional measures can we meet the deadline?
c) If the deadline is not realistic, what would be realistic?
d) asked differently: are there any charts or similar showing by how many percentage points the CM value decreases over a certain period during the readiness heating on average or under optimal conditions or or or?
Hello "Faydie". Your questions can be answered as follows:
If the functional heating has already taken place, then the possible thermal stresses, which a screed is later exposed to in the service condition, have already been achieved.
This means: you can heat the screed whenever and however you want if needed.
Screeds also dry without additional heating, that is nothing new.
Underfloor heating accelerates the drying process.
What makes sense: place a hygrometer in the room, run the underfloor heating (as it is currently only on standby to avoid reaching freezing temperatures) with 25°C flow temperature and watch whether the hygrometer reaches a value >70% relative humidity or not.
If the value is significantly undershot, it can be assumed that the maximum permissible residual moisture of 1.8 CM-% is undercut, then there is very likely nothing preventing the tiling work in February.
If you want to carry out a manual test:
Lay about 1m² of PE foil in the middle of the room on the screed and place the hygrometer under the foil.
Tape the edges of the foil securely with good adhesive tape and heat the screed at approximately 30/35°C flow temperature.
After 24 hours, check the hygrometer and also whether any condensate has formed under the foil.
If condensate drops are visible, the screed is certainly still too wet.
If no condensate drops are visible, the hygrometer should not show a value >70%.
This "manual test" is not made up but is a fairly reliable test with meaningful results!
I use it regularly when CM measurement marks were omitted (or forgotten) during screed installation and a reliable statement about the residual moisture of the screed is required.
----------------
Regards: KlaRa