CTA Aeroheat heat pump settings for improvement

  • Erstellt am 2020-10-15 11:59:56

ivenh0

2020-10-16 13:28:37
  • #1
Could it be related to the [Überstromventil]? During the last technician visit, he opened the valve quite a bit.
 

Daniel-Sp

2020-10-16 13:33:26
  • #2
then you would probably also have the problem during defrosting in heating mode
can you provide a DTA?
 

ivenh0

2020-10-16 13:42:36
  • #3
Yes, link will be sent via PM
 

Daniel-Sp

2020-10-16 14:00:21
  • #4
According to DTA, the defrost valve did not open. But it works in heating mode. A technician needs to take a look. Check with the manufacturer
 

ivenh0

2020-10-16 14:42:49
  • #5
Ok. Great. Thank you very much for the excellent analysis!

Are there any other points that should be configured differently on my heat pump so that it runs more efficiently?
 

Daniel-Sp

2020-10-16 15:46:37
  • #6
I haven’t checked that quickly now
 