Well, the specification of 15cm was somewhat misinterpreted by "hanghaus". The 15cm referred to the thickness of the screed. And now we come to the root cause analysis: Basically, such a thick screed is not necessary in a garage if it was installed as a bonded screed (which is to be assumed) and not above thermal insulation (i.e., floating screed, which is highly unusual in garages). Typically, installation thicknesses of about 25mm are sufficient. However, the probably existing installation thickness of 150mm is the main problem, in three respects. 1. It is impossible to install such a thick screed in a single layer with the necessary structural densification, 2. Such a thick screed is highly prone to cracking, and 3. It makes no sense at all to install such a thick screed as a load distribution layer. What insanely high loads are supposed to be absorbed by it????? (rhetorical question!) The crack has appeared; the subsequent trade (the coating applicator) recognized the crack beforehand and then also has to treat it accordingly so that the stresses do not impact his trade (the floor coating) in the future. The screed installer at the time is out of the picture since the coating applicator has deemed the substrate suitable and accepted it. And thus he is now the focus as your contact person. Do not let yourself be fobbed off here with pseudo-arguments! You did not order the crack; therefore, you do not have to accept it. Since I am familiar with the tricks of the trade: Be sure to write him a defect notice (this must be stated as such in the subject line!!) and request him, with a deadline (let’s say 5 weeks), to remedy the defect. How he does it is technically clear to me personally, but it is his trade, so HE has to consider it. ---------------------------- Regards and success: KlaRa