LudwigMuc
2025-04-25 17:03:17
- #1
Good day. We built a KfW 40 plus 3-family house with the company Rötzer Ziegel Element Haus. The construction phase of 8 months went very well. We have a heat pump from Daikin Altherma 3 H 16 HT with 13KW output. A buffer tank of 800 liters and a fresh water station in each apartment.
After moving in, we noticed that our hot water was only 36-41 degrees (due to hysteresis) at a flow temperature of 52 degrees and lost another 4 degrees with every shower. The temperature of the buffer tank was increased to 60 degrees and we had a water temperature depending on hysteresis between 42 and 48 degrees. After a hot bath, the water temperature dropped to 37 degrees. Then I found out that not the contractually agreed Straba W-FBR but an Oventrop regudis W-HTF had been installed in the apartments without our knowledge.
A comparison of the technical data shows that the Oventrop has significantly worse values.
Oventrop regudis W-HTF Staba W-FBR
Delta t 15 degrees 3-5 degrees
KW output 42KW 88KW
Draw-off rate 17 liters/minute 21 liters/minute
As a layperson but an engineer in retirement, looking at the values made it clear to me why we have to run with a flow temperature over 60 degrees to get water of 43-48 degrees. Since then, attempts have been made to convince us that there is no difference between the two stations and both are equivalent. The boiler was originally planned with 1000 liters but didn’t fit through the door anymore, so it was the 800-liter boiler. The company Oventrop also confirmed to us in writing that their FRIWAST in connection with a heat pump cannot be operated economically.
The look at the COP/yearly performance factor showed a value of 1.7 in January. After changes to the flow rate, differential pressure, and the position of the temperature sensors on the buffer tank, the COP/yearly performance factor dropped to 1.2 and the boiler temperature rose to 64 degrees. After another appointment, a return flow raise was implemented which caused a change of the COP/yearly performance factor to 0.81. When asked about this COP, the DAIKIN technician responded, "the values on the heat pump mean nothing; you would have to install a power meter on the heat pump and heat quantity meters in the supply and return flow" to obtain accurate values.
The warm water now lasts for 2 showers but to run 24/365 with a flow temperature of over 60 degrees is not something we find very good. Our preference would be a 400-liter hot water tank that is heated 1-2 times a day and the buffer tank would be operated with the usual flow temperature of about 35 degrees. The feasibility has already been checked by a heating engineer. I am not sure whether we should install a 400-liter hot water tank or replace the heat exchangers in the FRIWAST. Somehow, I have lost interest in the FRIWAST.
After moving in, we noticed that our hot water was only 36-41 degrees (due to hysteresis) at a flow temperature of 52 degrees and lost another 4 degrees with every shower. The temperature of the buffer tank was increased to 60 degrees and we had a water temperature depending on hysteresis between 42 and 48 degrees. After a hot bath, the water temperature dropped to 37 degrees. Then I found out that not the contractually agreed Straba W-FBR but an Oventrop regudis W-HTF had been installed in the apartments without our knowledge.
A comparison of the technical data shows that the Oventrop has significantly worse values.
Oventrop regudis W-HTF Staba W-FBR
Delta t 15 degrees 3-5 degrees
KW output 42KW 88KW
Draw-off rate 17 liters/minute 21 liters/minute
As a layperson but an engineer in retirement, looking at the values made it clear to me why we have to run with a flow temperature over 60 degrees to get water of 43-48 degrees. Since then, attempts have been made to convince us that there is no difference between the two stations and both are equivalent. The boiler was originally planned with 1000 liters but didn’t fit through the door anymore, so it was the 800-liter boiler. The company Oventrop also confirmed to us in writing that their FRIWAST in connection with a heat pump cannot be operated economically.
The look at the COP/yearly performance factor showed a value of 1.7 in January. After changes to the flow rate, differential pressure, and the position of the temperature sensors on the buffer tank, the COP/yearly performance factor dropped to 1.2 and the boiler temperature rose to 64 degrees. After another appointment, a return flow raise was implemented which caused a change of the COP/yearly performance factor to 0.81. When asked about this COP, the DAIKIN technician responded, "the values on the heat pump mean nothing; you would have to install a power meter on the heat pump and heat quantity meters in the supply and return flow" to obtain accurate values.
The warm water now lasts for 2 showers but to run 24/365 with a flow temperature of over 60 degrees is not something we find very good. Our preference would be a 400-liter hot water tank that is heated 1-2 times a day and the buffer tank would be operated with the usual flow temperature of about 35 degrees. The feasibility has already been checked by a heating engineer. I am not sure whether we should install a 400-liter hot water tank or replace the heat exchangers in the FRIWAST. Somehow, I have lost interest in the FRIWAST.