According to the energy certificate, do we not meet KfW 55?

  • Erstellt am 2017-07-22 13:11:20

Lagom

2017-07-22 13:11:20
  • #1
Hello everyone,

I have been following the forum for some time for interesting posts about construction since we will be starting soon. Usually, I was able to find the answers from existing posts, but with this topic I am a bit puzzled and hope you can help me.

Today I received the building application from our general contractor (incl. structural stability certificate and energy saving ordinance), a single-family house according to KfW 55 is to be built. However, a look at the created energy performance certificate makes me doubt a bit, as it looks to me as if we will not meet the standard.

Information about the single-family house
- Aerated concrete (36.5 cm)
- Central ventilation system with heat recovery (min. 88%)
- District heating (primary energy factor 0.70 %)

According to the energy performance certificate
Primary energy demand (q_p)
Actual value 40.1 kWh/(m*a^2) --- requirement value 56.3 kWh/(m*a^2) --> undershooting by -28.7%

Building envelope (H_t)
Actual value 0.26 W/(m^2*K) --- requirement value 0.38 W/(m^2*K) --> undershooting by -30.9 %

As far as I understand, the building envelope (H_t) is okay, but not the primary energy demand (q_p), this would have to be at least -45% to fulfill KfW 55.
Is this correct so far?
If I am right and the primary energy demand does not meet KfW 55 requirements, then the following statement from kfw.de confuses me

"The requirements for a KfW Efficiency House 55 are met if [...]"

"For the system technology, one of the 6 following system concepts must be implemented."

"2.) District heating with certified primary energy factor fp ≤ 0.7, central ventilation system with heat recovery (heat supply rate > 80 %)"

How does this fit together, according to the above statement KfW 55 is achieved but not according to calculation?

I hope you can help me, as we wanted to submit the building application on Monday to have a closed shell before winter.

Thanks in advance!

Best regards
Robert
 

Nordlys

2017-07-22 13:32:13
  • #2
Wouldn't it be easier and safer to be patient over the weekend and call the engineering office that issued the ID on Monday? Karsten
 

Lagom

2017-07-22 13:55:55
  • #3
Yes, I would definitely do that first thing on Monday. However, I wanted to hear another opinion on it, if someone is familiar with it or had a similar problem. By the way, which I forgot to mention, elsewhere the permissible maximum value (annual primary energy demand) is also given as 75.03 kWh/m^2. If I compare the calculated value with the maximum value (instead of the target value), then it also fits with KfW 55 ...
 

77.willo

2017-07-22 14:43:53
  • #4
Just multiply your demand by the factor of district heating. Then it will match quite accurately.
 

tempic

2017-07-22 14:54:58
  • #5
What you are quoting from the KfW refers to KfW55 according to reference values.

For you, KfW55 was calculated and therefore the corresponding sentence has no meaning for you.

I assume that what you call requirement values are the reference values of the Energy Saving Ordinance calculation. I would agree with you: your primary energy demand is too high ... it may be max 0.55x56.3=30.9 ... you have barely passed the Energy Saving Ordinance.

Why this is so, your energy consultant can tell you.

But if you have a KfW loan, it gets exciting now ...
 

Alex85

2017-07-23 09:42:53
  • #6


The primary energy demand already takes the factor into account.

But I find it strange that the primary energy demand is so high, when local heating with a factor of 0.7 is actually very good. In addition, there is the controlled residential ventilation with heat recovery, which significantly reduces the heating load (this could already be the error in the calculation) and thus reduces the energy demand for heating. The requirement value is, in my opinion, 64.35 kWh/(m²a) according to the Energy Saving Ordinance 2016, of which 55% = 35.3925.

H’T fits with 0.26, the target should be 0.28 for detached buildings.

Just ask. We are just laypeople here and all the rules for surcharges/deductions... well, at least I don't know them all.
 

Similar topics
10.05.2012Heating costs per year KfW55 - KfW70, building decision heating11
31.07.2013Ventilation system with heat recovery - sense or nonsense?18
19.06.2015Build according to KFW 70 or the Energy Saving Ordinance 201442
19.10.2015New energy saving regulation from 2016 -> What to build?30
23.10.2015Energy Saving Ordinance 2014 - Gas boiler without solar?38
10.01.2017Energy Saving Ordinance 2016 / KFW55 / Gas + Solar in 201628
07.07.2016Acceptance of single-family house: energy certificate16
22.09.2016Offer KfW70 house - KfW55 house already with additional controlled residential ventilation - Is KfW70 too airtight?12
03.04.2018New building KfW55 with gas, solar, and controlled residential ventilation with heat recovery43
24.04.2017Experiences Single-Family House KfW55 - Assigning Tradesmen Yourself?20
16.07.2017Energy Saving Ordinance, KFW55, KFW40 or KFW40 Plus19
09.09.2017District heating KfW55 - KfW70 costs Ventilation system/Exhaust system37
21.12.2017Energy saving regulation with gas boiler and heat recovery ventilation instead of solar?15
27.11.2017Ventilation system with heat recovery, installation location temperature11
25.11.2018Heating costs for Kfw55 - Electricity costs seem too high to me26
20.01.2020Build a multi-family house according to the Energy Saving Ordinance or KFW55?29
18.04.2021KfW 55 - Ventilation system yes/no? - Experiences222
03.11.2020Single-family house with KfW55/controlled residential ventilation or Energy Saving Ordinance standard - experiences and opinions?22
03.03.2021Purchase single-family house new build energy saving regulation standard prospectively sufficient?24
09.07.2021Building according to the Energy Saving Ordinance 2016 or KfW5543

Oben