What type of cable is needed from the fuse box to the stove connection?

  • Erstellt am 2021-11-06 11:32:09

RotorMotor

2021-11-07 13:31:20
  • #1
So, one may and can protect a 1.5mm² cable with 16A, depending on the length. With 3-phase, one may/can therefore draw 11kW.

This will never be exceeded by the cooktop-oven combination in any situation!

Addendum: It is really important that it is connected as 3-phase, otherwise there will be an overload of the neutral conductor!
 