Structural engineer: 2x 8mm reinforcement or 1x 16mm

  • Erstellt am 2017-03-29 09:53:29

pixelprof

2017-03-29 09:53:29
  • #1
How does the tensile strength of reinforced concrete (e.g., in horizontal beams) behave when I use 2 x 8mm reinforcement bars compared to 1 x 16mm? Or 2 x 6mm compared to 1 x 12mm? (Assuming identical components and the same steel quality.)
 

ypg

2017-03-29 09:55:58
  • #2
Wrong forum? Here are home builders :)

Regards, Yvonne
 

andimann

2017-03-29 10:48:27
  • #3
Hi,



Simply put:
just calculate the cross-sectional areas, that should answer your question:

Cross-section of the 8mm reinforcement: 50 mm^2 (4*4*pi)
Cross-section of the 16mm reinforcement: 200 mm^2 (8*8*pi)

The tensile strength of reinforced concrete is largely determined by the reinforcement. Replacing one 16mm bar with two 8mm bars is therefore not feasible; you would rather need 4 8mm bars.

In reality, it is probably not that simple, as there will be other influencing factors, such as the distribution and position of the reinforcement.

Regards,

Andreas
 