Simon-189
2024-06-10 06:53:29
- #1
Hello,
only the house manufacturer can confirm whether the calculated quality class was also used. I think you can ask again here and request a confirmation of the quality class.
The specification of the maximum deflection of L/200 can be found almost everywhere in the construction sector except for glass. That means profile length divided by 200 = maximum allowable deflection in the serviceability limit state, i.e. when floors, furniture, etc. are still present in the room. Let's assume one of the beams is 10.0m long (e.g. house width) and rests again in the middle on a supporting beam, resulting in a span length of 5.00m. 5000mm / 200 = 25mm deflection.
only the house manufacturer can confirm whether the calculated quality class was also used. I think you can ask again here and request a confirmation of the quality class.
The specification of the maximum deflection of L/200 can be found almost everywhere in the construction sector except for glass. That means profile length divided by 200 = maximum allowable deflection in the serviceability limit state, i.e. when floors, furniture, etc. are still present in the room. Let's assume one of the beams is 10.0m long (e.g. house width) and rests again in the middle on a supporting beam, resulting in a span length of 5.00m. 5000mm / 200 = 25mm deflection.