joschua_85
2022-10-14 17:17:27
- #1
Hello,
on 12.07 we had 7 cm of cement screed installed throughout the entire house. Because it wasn’t really urgent, we only started the heating program on 24.09. So it actually rested for a good 11 weeks.
The "roughest" part of the water is thus out, now it’s time for the floor coverings, which is why the Hotboy was turned on.
We have now heated according to the "program" of my heating engineer until 11.10, in consultation with the screed installer. I understand that this is not the "standard program," which I personally find desirable, because no new building still needs 55 degrees flow temperature today. The screed will never see that with our heat pump. MAX flow temperature according to calculation is 35 degrees.
We heated as follows:
1: 30 degrees
2: 35 degrees
3-5: 45 degrees (so the screed would experience it once)
6-12: 35 degrees
13-17: 40 degrees (after first quick test still too wet, therefore flow temp raised again)
18: 35 degrees
19: 30 degrees
But that should (hopefully) not be the topic. Much more, I am still puzzled that after such a long time, my tiler still finds a CM measurement unnecessary because his moisture meter (from GANN) still shows 65 digits. I understand the idea of testing beforehand.
But I don’t understand why it’s still all so wet?
Yes, I ventilate 3-4 times a day by cross-ventilation. I have 2 hygrometers in the house and ventilate as long as the humidity rises again. So actually always about 10 minutes. I don’t want to connect several construction dryers to the Hotboy now; that thing already heats you into bankruptcy anyway.
My questions:
Should I basically leave the windows tilted? Also at night? Or tilted + shock ventilation all day and closed at night? Still just shock ventilation?
Not ventilate at all when it rains? Warm and "full" air with water should go out, right? Is there a minimum flow temperature one should run?
Aside from the "special program," what else could it be?
Thanks to you all.
on 12.07 we had 7 cm of cement screed installed throughout the entire house. Because it wasn’t really urgent, we only started the heating program on 24.09. So it actually rested for a good 11 weeks.
The "roughest" part of the water is thus out, now it’s time for the floor coverings, which is why the Hotboy was turned on.
We have now heated according to the "program" of my heating engineer until 11.10, in consultation with the screed installer. I understand that this is not the "standard program," which I personally find desirable, because no new building still needs 55 degrees flow temperature today. The screed will never see that with our heat pump. MAX flow temperature according to calculation is 35 degrees.
We heated as follows:
1: 30 degrees
2: 35 degrees
3-5: 45 degrees (so the screed would experience it once)
6-12: 35 degrees
13-17: 40 degrees (after first quick test still too wet, therefore flow temp raised again)
18: 35 degrees
19: 30 degrees
But that should (hopefully) not be the topic. Much more, I am still puzzled that after such a long time, my tiler still finds a CM measurement unnecessary because his moisture meter (from GANN) still shows 65 digits. I understand the idea of testing beforehand.
But I don’t understand why it’s still all so wet?
Yes, I ventilate 3-4 times a day by cross-ventilation. I have 2 hygrometers in the house and ventilate as long as the humidity rises again. So actually always about 10 minutes. I don’t want to connect several construction dryers to the Hotboy now; that thing already heats you into bankruptcy anyway.
My questions:
Should I basically leave the windows tilted? Also at night? Or tilted + shock ventilation all day and closed at night? Still just shock ventilation?
Not ventilate at all when it rains? Warm and "full" air with water should go out, right? Is there a minimum flow temperature one should run?
Aside from the "special program," what else could it be?
Thanks to you all.