Questions about hydraulic balancing

  • Erstellt am 2024-01-11 09:51:03

Pacmansh

2024-01-11 09:51:03
  • #1
Hello,
I am currently in the process of balancing our heating system, end-of-terrace house, KfW55, net living area 145m², Vaillant Arotherm 75/5. I think I have understood the basic principle behind it, but I stumbled over two points.

The heating output on the ground floor was generally too high. I initially reduced the flow rate slightly on all circuits here. It was also easy to see that reducing the flow rate in one heating circuit increased the flow rate in others. That makes sense, of course. However, I assumed that this would also affect the flow rate in the heating circuit distributor on the upper floor. But it does not. Am I mistaken here? Is the flow rate to be set separately for each heating circuit distributor? In the master bathroom (upper floor), I currently have about 1.6 l set on the Taco, which is also the maximum adjustable value in the current configuration; I cannot open it further. I would like to try whether 2-2.5 l might bring somewhat higher temperatures.

Is it correct that the sum of all flow rates should roughly correspond to the flow rate of the pump on the Arotherm?
 

hegi___

2024-01-11 11:21:57
  • #2
One has a room-by-room heating load calculation carried out and calculates the flow rates based on this. Everything else is nonsense,
 

Pacmansh

2024-01-11 11:36:50
  • #3
Was done by the developer, the heating engineer said "this is shit", did it differently (better) and set roughly 1.5 l/m on all heating circuits on the ground floor and about 1 l/m upstairs. So much for the work of the professionals!
 

Jesse Custer

2024-01-11 11:45:09
  • #4


Help me out: what do "1.5 liters per meter" respectively 1 liter per meter – that is l/m – define??
 

Pacmansh

2024-01-11 11:51:34
  • #5
It should have said 1.5 l/min, sorry. Normal flow meters/Tacos are installed with a scale from 0 - 5 l/min.
 

Similar topics
27.08.2016Different window heights on the ground floor and upper floor14
21.02.2017Development plan difference between ground floor, roof, and single-storey17
17.12.2017Heating circuit distributor - position23
11.10.2021Actuators are open but no flow13
15.01.2022Floor plan planning semi-detached house, ground floor assessment20
04.05.2023Connection of heat pump to heating circuit distributor12
28.05.2025Floor plan: who has the master bedroom on the ground floor?54
02.10.2024Underfloor heating on the ground floor: insulate or not?16

Oben