Hello,

we are planning to lay laminate flooring in the basement. It is often said that a foil should be placed under the laminate in the basement.
Does this also apply if a vapor barrier has already been applied to the raw concrete?
And if so, why is a foil only required under the laminate in the basement, but not on the ground floor and upper floors?

Thanks!
 

KlaRa

2018-10-22 15:50:30
  • #2
Hello questioner. Laminate flooring is not suitable for the case that the corresponding basement room has already been assigned a subordinate use (thus not as living space) in its planning. A vapor retarder on the raw concrete slab does not protect the layers above (this also includes the cement screed) from slow dampening, because firstly a considerable residual amount of water always remains in a ground-contact concrete slab and secondly a vapor retarder cannot prevent a water vapor flow (there is no such thing as a "vapor barrier"; if anything, it is a seal or a vapor retarder). While a floor slab can release its residual moisture only "upwards," this is different with inhabited floor ceilings. There, the residual moisture of a concrete ceiling migrates upwards as well as downwards, depending on the vapor pressure gradient. Another note: In a pure basement room (thus not in a living space) there is no thermal insulation (and why should there be). If one were to lay laminate flooring on cold concrete there and use the room regularly, for example as an office, the dew point would be undershot on or possibly also under the laminate flooring elements. Air humidity can condense there as water. And because carrier boards for laminate flooring elements are usually made of moisture-sensitive wood-based materials, deformations and swelling cannot be excluded. However, there is an alternative for installation: laminate flooring elements suitable for installation in bathrooms. These carrier boards are moisture-resistant and do not deform (so easily). Good luck: KlaRa
 

cybergnom

2018-10-22 17:54:26
  • #3
Hello KlaRa,

thank you very much for the detailed answer.
Now, in our case, the basement is insulated on the outside and a 6cm styrofoam insulation (plus 2cm impact sound insulation) is laid on the vapor barrier. The entire basement has underfloor heating. One room is regularly used as an office.
In addition, a controlled residential ventilation system is installed.

Does the following still apply: foil under the laminate?
 

KlaRa

2018-10-22 18:27:11
  • #4
Hello questioner.
With the current additional information, it becomes clear that it is a living space located in the basement with a floating screed.
The basic rule here is: Yes, PE foil is necessary as a vapor barrier!
Regards: KlaRa
 

Scout

2018-10-24 12:38:11
  • #5
if I may join in here:

in our basement, a sealing membrane with bitumen (A*ujet) was laid on the floor slab made of WU concrete, followed by polystyrene insulation and screed.

Is a PE foil still needed here or can the screed be covered directly with elastic coverings such as linoleum or rubber?
 

KlaRa

2018-10-24 13:58:06
  • #6
WU concrete, that is concrete made to be "waterproof," is always permeable to water vapor! In physics and building physics, we differentiate between the different states of matter. Thus, WU concrete allows water to penetrate the cross-section only to a limited extent under a water column of up to 5 bar (I think it is about 5 cm). The water vapor pressure, on the other hand, "marches" through the structure regardless of the w/c ratio, always following the lower partial pressure. In the case of a slab on the ground, the lower pressure is always in the space above it.
This means: YES, a PE foil should also be installed as a vapor barrier here on the screed. This still corresponds to the current state of the art as well as to the majority of the installation instructions from manufacturers of floating laminate floors (unless these have been approved by the manufacturer for wet rooms).
Regards: KlaRa
 

Similar topics
14.01.2013Insulation / Vapor Barrier Top Floor Ceiling / Collar Beam, Open Ceiling14
21.08.2014Insulation on upper floor concrete ceiling / roof by own work - vapor barrier?10
15.05.2015Own contribution: Determination of residual moisture10
28.04.2016Order screed - plaster14
07.08.2016Upper floor without screed - only concrete floor15
22.12.2016Is rain harmful to concrete slabs?12
20.08.2016Base slab vs strip foundation15
02.10.2016Vapor barrier vs vapor retarder21
29.07.2018Perimeter insulation under the floor slab and still XPS under the screed?28
10.07.2017WU concrete + flush-mounted boxes in the residential basement - how can this be solved?35
01.07.2017Roof construction - Which type of vapor barrier?10
06.10.2019Base plate with concrete core activation. What is your opinion?46
20.05.2018Dense, well-insulated wooden house without plastic? (Vapor barrier)21
31.10.2018Concern about vapor barrier - air from ceiling outlet12
03.02.2019Underfloor heating in the floor slab - advantages and disadvantages?15
17.08.2019Base plate - Reinforcement steel is sticking out12
02.10.2019Base plate - film against rising moisture15
13.04.2020Insulation in the construction trailer, vapor barrier yes/no?12
12.11.2020Formwork blocks on the foundation slab in a mortar bed or not?13
07.05.2023Is it sensible for the expert to inspect the base plate?55

Oben