Floor construction, screed, low height

  • Erstellt am 2024-06-17 23:25:38

Gotop09

2024-06-17 23:25:38
  • #1
Hello everyone,

I have been puzzling over our floor construction for weeks and wanted to ask around...

We have an old house built in 1966 and now want to renovate completely, including new underfloor heating on the ground floor, first floor, and attic. There is a basement as well, but it's not heated.
The existing floor buildup is very minimal and with insulation, screed, and covering only about 6.0 - 6.5 cm.
Basically, I wanted to remove everything first and then lay a floating screed including the 16mm floor pipes on a proper insulation layer.

After consulting various screed contractors, I am now more confused than ever, everyone says something different...
One recommends the Schlüter studded panels because they only require 0.8 cm pipe coverage, but I then saw that the panels alone are already 4.4 cm thick, so that puts me back at at least 5.2 cm, I am calculating about 5.5 cm plus insulation around 2 cm? That would be a total of 7.5 cm plus covering.

Another recommends a solution with Retanol additives, which could reduce the coverage to about 2.5-3.0 cm, so with floor pipes about 4.5 cm plus insulation I would be at 6.5 cm plus covering. That doesn't sound bad at first, but it's probably really expensive, since no price has been given to me yet...

The third would leave out the insulation and build up entirely conventionally, with about 6.5 cm total plus covering.

Does anyone also have tips on whether to use cement screed or calcium sulfate? I know cement screed is good for wet rooms and outside, whereas calcium sulfate conducts heat better but should not get wet. But how about the Retanol additives? Or are they only for cement screeds anyway?

And what do you say about 2 cm thermal insulation? Can you get something decent with that? According to which classification or product should I look?
Or how about leaving out the insulation? Or insulating from below on the basement ceiling? Does that even help? Basement height is almost 2.2 m.

I hope I have included as much information as possible for now, I am happy to answer further questions.
I would be grateful for any advice first of all!
Best regards
 

nordanney

2024-06-18 07:21:52
  • #2

Both work practically equally well – regardless of whether it’s a wet room or not.

I had a similar setup. "Proper" insulation on the ceiling is nonsense if you can properly insulate the basement ceiling from below (e.g., 10-12cm PUR).
Suggestion: Use 20mm PUR aluminum-coated for the insulation on the ceiling. On top of that, staple the underfloor heating pipes directly (there are suitable grid films for this) and have a thin screed laid – whether with Retanol or other products. The surcharge is manageable, and if you add an accelerator, you will recover the extra costs through, for example, a screed that dries 4 weeks faster.
 

Gotop09

2024-06-18 09:16:42
  • #3


So, first of all, thank you very much for your incredibly quick feedback!

Would you actually do both on the basement ceiling, meaning insulate from below and above? Or would that be redundant and basically unnecessary?
Or is the 20mm insulation layer on the ceiling more to be seen as impact sound insulation?
I have basically ignored the impact sound insulation topic so far because I thought I wouldn’t have any building height for that anyway, and a 20mm insulation hopefully brings a bit of sound improvement too!?
 

nordanney

2024-06-18 10:46:54
  • #4
If you later hold a thermometer to the cellar ceiling, then you will know that you should have insulated it better. So yes, if you want to heat the living spaces and not the cellar with the underfloor heating, then proper insulation is absolutely essential (you will also notice this in the heating costs). See it as light insulation and as a base on which the pipes can be stapled. You can almost disregard impact sound insulation since you only have the cellar beneath the rooms. Nobody is bothered by impact noise there.
 

Gotop09

2024-06-19 11:39:13
  • #5


Thank you very much! That already sounds really good!
Let me quickly summarize:
Insulate the basement ceiling from below with 10-12cm
Then, on the ceiling, first 2cm insulation board plus foil, then staple the underfloor heating pipes on top, and then cover with as thin a screed as possible. If possible with an additive (Retanol) to reduce the thickness and drying time.
I then probably come to about 6.5cm build-up height plus covering means about 7.5cm. That's about 1.5cm more build-up height than existing, but I think I can live with that.

Regarding impact sound, I just hope the 2cm insulation layer helps a bit. For the basement it's of course irrelevant, but on the upper floor and attic the same floor construction should apply. So does that mean I just shouldn't complain and should put up with the kids?
Or is there maybe a tip for that? I guess a few millimeters of impact sound insulation on the screed is nonsense with underfloor heating, right?
Oh, and we planned laminate flooring, can I then safely lay it directly on the screed or do I need an underlay?

And do you actually need a vapor barrier between the raw ceiling and insulation, see picture? Or what exactly is that?
Best regards
 

Harakiri

2024-06-19 13:00:01
  • #6
I believe that with 2 cm PIR/PUR insulation laminated with aluminum foil, it becomes a bit tight to use staples. In any case, make sure that the boards (of this thickness) are approved for stapling, and pay attention to the length of the staples. However, there are also hook-and-loop systems that work almost just as well.

PIR/PUR alone is not suitable for impact sound insulation. However, there are composite boards that combine PIR/PUR with EPS and, in a way, bring together the advantages of both materials. But then the thickness is correspondingly greater.

But as long as the ground floor (EG) and attic (DG) are in the same "climate zone" regarding underfloor heating, it is not necessary to install expensive PUR in the attic—there you do not basically need insulation if the rooms are heated relatively evenly.
 

Similar topics
12.02.2013Heating single-family house, underfloor heating conversion, insulation, gas boiler defective19
06.03.2013Pump noises in underfloor heating, pump in living room, noise disturbance13
30.03.2015Underfloor heating in the bathroom sufficient or additional heating - wall heating?22
22.08.2014Underfloor heating or not?20
20.03.2015Tiles, vinyl, or other types of flooring with underfloor heating?23
14.08.2015Underfloor heating or radiators?12
20.10.2015Underfloor heating on the ground floor and upper floor, radiators in the basement?15
08.02.2017Underfloor heating connections in the wrong room13
22.06.2017Quality impact sound insulation10
13.11.2017Which impact sound insulation is suitable for underfloor heating?15
16.01.2021Impact sound insulation - Which values are important for impact sound?11
27.11.2018Evaluation of wall construction - steel frame prefab house11
01.03.2020Protective pipe for underfloor heating forgotten in the area of movement joints39
14.02.2021Old building renovation, underfloor heating, electricity, water, possible pitfalls, etc.11
08.03.2021Screed qualities in the field of anhydrite / cement screed11
22.11.2023Very low construction height with underfloor heating in old buildings11
25.11.2022Mill underfloor heating or apply new screed?17
04.07.2023New cement screed wobbles on new underfloor heating and insulation15
02.10.2024Underfloor heating on the ground floor: insulate or not?16

Oben