Does the structural builder have to paint the transition between styrofoam and brick wall black?

  • Erstellt am 2018-03-05 22:28:41

Marchonisch

2018-03-05 22:28:41
  • #1
Good evening

Today I had a plasterer here who is supposed to do the exterior plaster for us.

When we walked around the house together, he said that our shell builder should first paint black the transition from the Styrofoam to the brick wall (outside).

We built on a slope. Our floor is underground.

The concrete walls are painted black and covered with the mentioned Styrofoam.

It sounds logical, but the shell builder immediately said that it doesn't have to be done. He even said that the black bitumen could penetrate into the wall...

What do you say about this? I am also surprised that the second plasterer said nothing about it.

 

Marchonisch

2018-03-25 12:07:24
  • #2
No one has an idea or opinion about that?
 

mertmk3

2018-03-29 13:19:45
  • #3
At our company, the bituminous thick layer is applied up to above the first row of bricks on the ground floor, as well as the perimeter insulation and [Noppenbahn]. Above that, wider bricks without a bituminous thick layer are used.
 

Curly

2018-03-29 13:37:10
  • #4


At our place, a coating was also applied up to above the second row of bricks, but I can't remember what it was called, it was gray.

Best regards
Sabine
 

Knallkörper

2018-03-29 14:04:18
  • #5


That was probably a sealing slurry.

On the topic: How is it supposed to be prevented that surface water penetrates under the first row of stones? There is a sealing membrane between the floor slab and the masonry there. In its current condition, it is ineffective.

The masonry at the top left in the picture looks somewhat adventurous. How far does the masonry protrude above the intermediate ceiling?
 

Benutzer 1003

2018-03-29 16:51:02
  • #6
Hello forum,

The sealing against moisture from the ground is regulated by DIN 18195 and DIN 18533.

Accordingly, the sealing must be elevated at least 15 cm above the planned maximum water level (ground surface). Therefore, I would classify the work as defective.

According to the aforementioned standards, a special expert plan (architect) must be created for sealing measures. Has this been done?

If not, it is initially a planning defect.

Regardless, the executing company has the so-called duty to inform. The contractor should have recognized the defective planning and pointed out the expected defects.

If this has not happened, it is an execution defect.

I would document the situation and report the defects in detail. A deadline of 1 week for defect rectification is sufficient. Afterwards, rework should be refused and substitution threatened.

I would definitely stop the continuation of the work until the sealing has been properly installed. Retrofitting will be difficult to impossible.

Due to the complexity, I would involve an expert with the corresponding field of expertise.

Best regards

Kristof
 

Similar topics
07.09.2012Single-layer masonry vs. double-layer masonry with ETICS19
19.11.2013Walls made of Styrodur or Styrofoam?10
27.03.2014Interior walls upper floor lightweight construction instead of masonry?12
22.07.2017Horizontal sealing of the base slab24
09.11.2019Sound problem: Does noise come through masonry - through the exterior plaster?20
21.10.2017Sealing the base slab before the roof is installed19
15.10.2018Is the shell construction overloaded? Current situation in the construction industry!13
18.10.2018Liability for various defects after acceptance of the property19
08.11.2018Structural shell / Structural shell cost calculation - How does it calculate?52
03.09.2019Should the gap transition from the roof box to the masonry be closed or not?11
12.07.2023Sealing of floor-to-ceiling windows from the outside74
09.03.2021Withholding payment for defects in the shell construction74
11.05.2021Which masonry is suitable for noise level range III24
10.07.2021Is basement waterproofing available in the old building from 1971?12
15.07.2021Balcony slope and waterproofing costs12
24.12.2021GU insolvency after acceptance - Open defects15
03.06.2022Masonry - Closing/filling the wall behind the underfloor heating manifold14
17.08.2022Masonry is crumbling! Is there a risk of collapse?15
10.10.2023Disposable e-cigarette disposed of in the masonry13

Oben