Can the apartment ventilation system of controlled residential ventilation enter the sheds?

  • Erstellt am 2022-06-11 00:22:45

karl.jonas

2022-06-11 00:22:45
  • #1
Most of the time, the apartment ventilation system of the controlled residential ventilation is seen in the utility room, basement, or attic. I have not planned K+S; the space in the utility room is tight. But I have a shed right next to the planned house (wall to wall). Is there any reason against mounting the ventilation system outside the house? A positive side effect would be that the device would certainly not be heard. From when do the lengths of the ventilation ducts become a problem?
 

PhiIipp

2022-06-11 07:34:12
  • #2
If your shed is heated, then that is not a problem.
You only need to pay attention to the penetration into the building.
If your shed, which I assume, is not heated, then that won't work. The devices are designed to operate at room temperature. The same applies to the pipes. You would have to insulate them at great expense.
The device itself, of course, too. And by this point at the latest, your admittedly good idea becomes uneconomical. The device would have to be put into a kind of enclosure so that it is still accessible. You normally cannot do that yourself.
 

karl.jonas

2022-06-11 09:31:57
  • #3
Thank you very much for the quick and comprehensible answer. So the device will be placed in the apartment.
 

Dogma

2022-06-11 22:28:15
  • #4
If your shed has at least 10 degrees, it is not a problem for the controlled residential ventilation itself. The only thing you need to manage with Armaflex are the cold bridges on the pipes (into the thermal envelope of the house and possibly also the supply and exhaust air). By the way, there are also controlled residential ventilation systems that are installed on the ceiling (about 30 cm device + about 5 cm hanger), so if you don't have much space on the walls, that might be a solution for you.
 

WilderSueden

2022-06-11 22:50:14
  • #5
has outsourced his technical room to a separate little building if I remember correctly.
 

i_b_n_a_n

2022-06-12 08:09:42
  • #6
correct. However, this room is very well insulated except for the door, even though it is not part of the thermal envelope. Although not heated, all the technology is housed there, so it never gets completely cold...
 

Similar topics
09.04.2012Decentralized vs. Central Controlled Residential Ventilation? Points for KfW House Calculation20
26.07.2012Ventilation with controlled residential ventilation system15
24.12.2012Is controlled residential ventilation in this case sensible or not?10
25.08.2014Decentralized residential ventilation, exhaust air heat pump - experiences?10
01.08.2014Water-bearing wood stove (supplement to the air-water heat pump and controlled residential ventilation with heat recovery)?10
03.06.2015Controlled residential ventilation with heat recovery --- a confusing maze?12
07.07.2017Experiences with decentralized controlled residential ventilation?13
09.09.2016Controlled residential ventilation and disc valve - Passive House21
22.09.2016Offer KfW70 house - KfW55 house already with additional controlled residential ventilation - Is KfW70 too airtight?12
14.05.2017Building drying: Is it better to turn off the controlled residential ventilation system in summer?12
04.06.2017Which type of controlled residential ventilation are we?10
27.07.2017Install controlled residential ventilation ducts without a basement?12
10.06.2019Controlled residential ventilation - Is stage 7 out of 9 an acceptable design?22
29.04.2018Gas heating + solar & controlled residential ventilation or air-water heat pump Energy Saving Ordinance 201626
29.10.2018Decision Controlled Residential Ventilation: Helios EC 300 W R vs. HomeVent comfort FR 30112
04.09.2018Pantry: Is a heating coil sensible in controlled residential ventilation?14
05.03.2020Carport with massive shed30
04.12.2020Tips for a sports shed or garage?18

Oben