Hello dear heating professionals,
we are currently in the process of planning our heating system with the heating engineer. In the last few days, there has been a lot of talking and discussing between the architect, energy consultant, and heating engineer, as the calculations from HB and the energy consultant were far apart. But first things first.
The energy consultant originally calculated the following heating load for our house using the simplified method (DIN EN 12831-1:2017-09 sec. 8):
NAT -16°
Room temperature +20°
Ht= 0.261 W/(m2K)
Heat transfer surface area A 584.8 m2
Building air exchange at NAT nGeb 0.50 h-1
Air volume V 745.6 m3
= Building heating load 10.1 kW
The heating engineer offered us a Stiebel Eltron LWZ 5 S Plus. I then noted as a layman that 10 kW vs. 5 kW somehow sounded illogical and that 10.1 kW seemed quite high to me. The calculation was then adjusted, as the NAT for my postal code is -10°. With otherwise unchanged parameters, the energy consultant now calculates a building heating load of 8.4 kW. But even here, from my layman’s perspective, 8.4 kW stands opposite the 5 kW of the heat pump.
However, the product information states that the air-to-water heat pump is recommended up to 8.0 kW (see attachment).
The reason for all the differences is supposed to be that the building heating load was calculated according to DIN 12831, and the heat output of the LWZ is based on EN 14511. Thus, everything is supposed to match.
The statement from the heating engineer was also that in all living rooms we lay 15 cm and in the bathrooms we put in as much as possible.
A few more info about our single-family house: KFW 55 monolithic with 36.5 Poroton. Ground floor + upper floor 171 sqm (completely heated) as well as a partially heated basement. The heated floor area in the basement is an additional 29.3 sqm.
And to add to the confusion, I used the often quoted online heating load calculator (1st Google search result for “Energieeinsparverordnung-Heizlastabschätzung”) and come to a heating load of 5.25 kW with the listed parameters.
I’m completely lost now. Three heating loads, two standards, what now?
Thanks very much for your input. I would be happy if some light is shed on the matter.

we are currently in the process of planning our heating system with the heating engineer. In the last few days, there has been a lot of talking and discussing between the architect, energy consultant, and heating engineer, as the calculations from HB and the energy consultant were far apart. But first things first.
The energy consultant originally calculated the following heating load for our house using the simplified method (DIN EN 12831-1:2017-09 sec. 8):
NAT -16°
Room temperature +20°
Ht= 0.261 W/(m2K)
Heat transfer surface area A 584.8 m2
Building air exchange at NAT nGeb 0.50 h-1
Air volume V 745.6 m3
= Building heating load 10.1 kW
The heating engineer offered us a Stiebel Eltron LWZ 5 S Plus. I then noted as a layman that 10 kW vs. 5 kW somehow sounded illogical and that 10.1 kW seemed quite high to me. The calculation was then adjusted, as the NAT for my postal code is -10°. With otherwise unchanged parameters, the energy consultant now calculates a building heating load of 8.4 kW. But even here, from my layman’s perspective, 8.4 kW stands opposite the 5 kW of the heat pump.
However, the product information states that the air-to-water heat pump is recommended up to 8.0 kW (see attachment).
The reason for all the differences is supposed to be that the building heating load was calculated according to DIN 12831, and the heat output of the LWZ is based on EN 14511. Thus, everything is supposed to match.
The statement from the heating engineer was also that in all living rooms we lay 15 cm and in the bathrooms we put in as much as possible.
A few more info about our single-family house: KFW 55 monolithic with 36.5 Poroton. Ground floor + upper floor 171 sqm (completely heated) as well as a partially heated basement. The heated floor area in the basement is an additional 29.3 sqm.
And to add to the confusion, I used the often quoted online heating load calculator (1st Google search result for “Energieeinsparverordnung-Heizlastabschätzung”) and come to a heating load of 5.25 kW with the listed parameters.
I’m completely lost now. Three heating loads, two standards, what now?
Thanks very much for your input. I would be happy if some light is shed on the matter.