Hello everyone.
Briefly about the system.
Air-water heat pump Elco with underfloor heating, 9.93kWh photovoltaic system and KWR with central heat recovery.
I have now removed the electric actuators for the thermal balancing and want to set the system this way over the winter. I want to make the adjustment now via the "float valves". In which direction do these need to be turned for more or less flow? Do I need to pay attention to anything?
Currently, the settings are as they were made during the hydraulic balancing.
The heating curve is set to 2 out of 10 and the reference outside temperature to 12.
Currently, heating is only on at night.
The delay time is set to 5 minutes. After this time window, the heating turns off above 12 degrees and turns on below 12 degrees. Would you change this value?