Hi,
in load case W.2-1E, the fully welded PYE PV 200 S5 on the base plate is basically state of the art. Under the masonry, a layer of G 200 DD is traditionally laid as a cavity barrier. But: this is not welded to the surface waterproofing, rather it lies loosely to be able to absorb movements. The surface waterproofing runs under the wall, if possible, otherwise it should be neatly finished each time so that no water gets behind the barrier layer. Is it specified in detail whether you have a bonded or loose masonry bed? Because that could still influence the wall structure.
Good luck!
in load case W.2-1E, the fully welded PYE PV 200 S5 on the base plate is basically state of the art. Under the masonry, a layer of G 200 DD is traditionally laid as a cavity barrier. But: this is not welded to the surface waterproofing, rather it lies loosely to be able to absorb movements. The surface waterproofing runs under the wall, if possible, otherwise it should be neatly finished each time so that no water gets behind the barrier layer. Is it specified in detail whether you have a bonded or loose masonry bed? Because that could still influence the wall structure.