Is the electrician's work correct?

  • Erstellt am 2021-07-21 12:17:44

AllThumbs

2021-07-21 12:17:44
  • #1
Hello everyone,

I looked at the electrician's work today. At one point where 7x1.5mm² should have been installed, 5x1.5mm² + 3x1.5mm² was installed instead. However, this would mean I am missing an L conductor. Or would the "2nd neutral conductor" of the 3x1.5mm² cable also be allowed to be used as L?
 

HarvSpec

2021-07-21 13:21:53
  • #2
Green/Yellow and Blue are reserved for Earth and Neutral conductor
 

Sahitaz

2021-07-21 13:53:13
  • #3
Green/yellow is definitely to be used for earth/PE, legally. Blue as neutral conductor is nice to have, but may certainly be used as a switching conductor or similar. So what your electrician is doing is absolutely fine. At least that was still the case during my apprenticeship (8 years ago).
 

AllThumbs

2021-07-21 14:27:03
  • #4



Hmm, now I have 2 opposing opinions o_O
Unfortunately, I haven't found anything about it on Google either.
 

HarvSpec

2021-07-21 14:50:41
  • #5
There is no legal requirement (as far as I remember) that blue must be the neutral conductor.
 

Sahitaz

2021-07-21 14:54:29
  • #6
The use of conductor colors is specified in standards [2] and [3]. Both regulations contain the following, essentially consistent statements:
• If a circuit contains a neutral conductor marked by color, the conductor marked blue or light blue must be used for this purpose.
• If no neutral conductor is required, the blue marked conductor may be used for any other purpose, but not as a protective conductor.
 