buderus_friwa
2024-01-15 00:14:24
- #1
Hello,
I have installed a fresh water station (Buderus FS 2) on a buffer tank (Buderus PNR750-C).
Unfortunately, the temperature of the hot water produced by the fresh water station fluctuates greatly!
Attached is a picture showing the enormous fluctuations.
The fresh water station produces hot water (at a buffer tank supply temperature of 70 degrees) sometimes at 62 degrees Celsius and sometimes down to about 25 degrees Celsius.
Showering is a nightmare when the hot water temperature uncontrollably swings up and down by up to 40 degrees.
Possible causes such as too low a buffer tank temperature can be ruled out (it is consistently high at about 70 degrees).
The draw-off rate of 8 liters/min is also well below the performance of the Buderus FS 2 of 22 liters/min.
The temperature of the incoming cold water is also constant. There were no other simultaneous draw-offs either.
The primary pump in the fresh water station also shows no error.
(The entire system consists of a Buderus Logaplus package S94 together with the Logaplus package K33/2)
What else could it be? I look forward to all ideas. As it fluctuates now, the Buderus fresh water station is unfortunately totally unusable :-(
Best regards!
I have installed a fresh water station (Buderus FS 2) on a buffer tank (Buderus PNR750-C).
Unfortunately, the temperature of the hot water produced by the fresh water station fluctuates greatly!
Attached is a picture showing the enormous fluctuations.
The fresh water station produces hot water (at a buffer tank supply temperature of 70 degrees) sometimes at 62 degrees Celsius and sometimes down to about 25 degrees Celsius.
Showering is a nightmare when the hot water temperature uncontrollably swings up and down by up to 40 degrees.
Possible causes such as too low a buffer tank temperature can be ruled out (it is consistently high at about 70 degrees).
The draw-off rate of 8 liters/min is also well below the performance of the Buderus FS 2 of 22 liters/min.
The temperature of the incoming cold water is also constant. There were no other simultaneous draw-offs either.
The primary pump in the fresh water station also shows no error.
(The entire system consists of a Buderus Logaplus package S94 together with the Logaplus package K33/2)
What else could it be? I look forward to all ideas. As it fluctuates now, the Buderus fresh water station is unfortunately totally unusable :-(
Best regards!