Compressor broken after 6 years (Ecoforest ground heat pump / well construction Heth)

  • Erstellt am 2023-03-24 09:38:55

jx7

2023-03-24 09:38:55
  • #1
After 6.5 years, the compressor of our ground source heat pump is broken.

The lifespan of such compressors is stated to be 25-30 years.

Has this ever happened to anyone else?

Was the heat pump possibly installed incorrectly or what caused the damage?

In addition:
The installing company Brunnenbau & Erdwärme Heth from Lorsch refuses to carry out the repair, citing a shortage of skilled workers.

Overall, no official Ecoforest partner could be found to perform the repair; a local climate and refrigeration company will now take over the repair.

It is an Ecoforest geothermal heat pump (Model C3 3-12KW HTR EH) with a Copeland Scroll compressor ZPV36K1E-1E9-130.

Was the 12kW heat pump perhaps oversized for our house ([Es laufen 190 qm Fußbodenheizung und das Warmwasser für 5 Personen über die Erdwärmepumpe]. The house is almost KfW-55 standard: final energy demand: 21.4 kWh/(m^2*a) / primary energy demand: 51.4 kWh/(m^2*a) / energetic quality of the building envelope: 0.25 W/(m^2*K))?
 

KarstenausNRW

2023-03-24 11:08:03
  • #2

Sometimes things just break. That's bad luck - nothing more, nothing less. It's just a technical device.
The lifespan is not determined by years, but the years are calculated based on average usage. If you now have a heat pump that starts up 56 times a day (this is called cycling), then the average usage for you might already be reached after 6.5 years.

Only the specialist company carrying out the repair can tell you exactly what is defective and why.
 

jx7

2023-03-24 11:20:46
  • #3
Yes, bad luck is an option.

I understand that a device with a lifespan of 25-30 years can also last only 15-20 years or sometimes 35-40 years.

But only 6.5 years is very little and very annoying.

The display of the [Erdwärmepumpe] shows:
Hours: 19672
Starts: 57579
Starts/hour: 35.596

The suspicion of oversizing comes from the specialist company. Let's see how it goes.
 

WilderSueden

2023-03-24 11:23:28
  • #4
With a runtime of 2 minutes per start, probably more is wrong than just the sizing
 

RotorMotor

2023-03-24 11:30:06
  • #5
Yes, that is really bad.
Maybe it was incorrect settings or problems with the hydraulics like ERR closing too often, etc.
And definitely also oversized.
 

andimann

2023-03-24 12:03:45
  • #6
Hello,

Something doesn’t add up in your values. Has a comma been misplaced somewhere?



6.5 years are about 57,000 hours. That would give you a start/hour (which I also think is way too high). And a running time per start of 1/3 h = 20 minutes per start.
What does the "Starts/Hour 35.596" mean then?

Best regards,

Andreas
 

Similar topics
27.10.2013Geothermal heat pump maintenance: what to watch for and how22
12.01.2012Geothermal heat pump, solar, and fireplace as heating?15
09.05.2015Ground source heat pump vs. air source heat pump24
30.12.2016Geothermal heat pump with controlled living space ventilation or without18
11.07.2018Economic efficiency of geothermal heat pump10
27.09.2020Sound insulation of geothermal heat pump in the technical room17
10.04.2021Geothermal heat pump for a small single-story single-family house15
01.01.2022Geothermal heat pump or gas boiler - experiences?17
22.03.2023Expand ground source heat pump to heat a small indoor pool18
05.03.2024Is a buffer tank useful in a heat pump?72
28.02.2024Repair the heat pump for €5,000-7,500 or replace it with a new heat pump?18

Oben